I'm working up a proposal to upgrade a service to a three family in Boston. It's a 3 decker.
The landlord lives in one of the units and wants some wiring done in her unit and one other. Mostly kitchen remodel stuff but my questions are about the service for now.
The existing service is (I'm guessing) 100 amps coming into the basement and hitting three meter sockets which each feed ing an apartment panel right above. The incoming conduit is 1-1/4" GRC. I will check with the POCO but I think they will require the new meter sockets outside even though most I see in the neighborhood are inside.
What I don't understand is how the existing arrangement met code. Each apt panel has about 10-12 breakers each and the panels have no main CB's. In this arrangement, isn't the limit 6 total CB's to shut down the power to the building? That would be just two CB's per panel. I don't get why these panels don't have MCB's???
I am planning to upgrade the service to 200 amps with four meters and four panels. The fourth panel will be to connect to common area loads that the landlord will pay for. I plan to feed each of the four new panels with 100 amps. I have never done a multi-family service upgrade before so I am describing my plans in case anybody here can forsee any problems.
The landlord lives in one of the units and wants some wiring done in her unit and one other. Mostly kitchen remodel stuff but my questions are about the service for now.
The existing service is (I'm guessing) 100 amps coming into the basement and hitting three meter sockets which each feed ing an apartment panel right above. The incoming conduit is 1-1/4" GRC. I will check with the POCO but I think they will require the new meter sockets outside even though most I see in the neighborhood are inside.
What I don't understand is how the existing arrangement met code. Each apt panel has about 10-12 breakers each and the panels have no main CB's. In this arrangement, isn't the limit 6 total CB's to shut down the power to the building? That would be just two CB's per panel. I don't get why these panels don't have MCB's???
I am planning to upgrade the service to 200 amps with four meters and four panels. The fourth panel will be to connect to common area loads that the landlord will pay for. I plan to feed each of the four new panels with 100 amps. I have never done a multi-family service upgrade before so I am describing my plans in case anybody here can forsee any problems.