This applies to emergency power on a backup generator.
I have an 80 amp OCPD feeding a downstream 200 amp OCPD (selectively coordinated) which is dialed down to 80 amps. Since the 200 amp OCPD has the possibility of being dialed back to the full 200 amps do the feeder conductors have to be sized to 200 amps (#3/0) or can they be sized at 80 amps (#3)? I cannot find a code requirement for this type of question.
I have an 80 amp OCPD feeding a downstream 200 amp OCPD (selectively coordinated) which is dialed down to 80 amps. Since the 200 amp OCPD has the possibility of being dialed back to the full 200 amps do the feeder conductors have to be sized to 200 amps (#3/0) or can they be sized at 80 amps (#3)? I cannot find a code requirement for this type of question.