Arc fault.

Status
Not open for further replies.

Reddy_kW

Member
Location
NC
We had an arc fault event here at work. A 13.8 kv motor faulted in the peckerhead. The relay techs that came out said it was a 20,000 amp fault and it lasted 6 cycles. It blew the box open, popped the heads off of about 50-60 5/16" bolts. My question is, how can I determine the cal/cm2 of the incident? I know I need to have more info, but I'm curious to know the energy created here.

photobucket-10818-1353593662617_zps490a871d.jpg


photobucket-44956-1353593743649_zpsffe60b82.jpg


photobucket-55115-1353593872718_zpsac929bfb.jpg


photobucket-39557-1353594331542_zps563de6ea.jpg
 

Reddy_kW

Member
Location
NC
Thanks, but I believe it may be a little over my head. If I plug in 24" for working distance, after running the numbers I'm getting an answer in the neighborhood of 250 billion? My math doesn't seem to be telling me what I think it should after reading that article and plugging numbers.
 

ghostbuster

Senior Member
With a trip time range from .051 to .111 sec (6 cycles is approx..096 sec) incident energy is approx. 1.8 cal. at 36" with 20 ka. of fault current (SKM arc fault program)
 

G._S._Ohm

Senior Member
Location
DC area
Seems like this equation


EMB = 1038.7 DB-1.4738 ? tA [0.0093 F2 0.3453 F + 5.9673]

should be

= 1038.7 X DB^-1.4738 X tA X [(0.0093 X F^2) - (0.3453*F)+ 5.9675)]
The minus sign was missing in the first example.

You can cut and paste this second equation right into an Excel cell.



 
Last edited:

ATSman

ATSman
Location
San Francisco Bay Area
Occupation
Electrical Engineer/ Electrical Testing & Controls
We had an arc fault event here at work. A 13.8 kv motor faulted in the peckerhead. The relay techs that came out said it was a 20,000 amp fault and it lasted 6 cycles. It blew the box open, popped the heads off of about 50-60 5/16" bolts. My question is, how can I determine the cal/cm2 of the incident? I know I need to have more info, but I'm curious to know the energy created here.

photobucket-10818-1353593662617_zps490a871d.jpg


photobucket-44956-1353593743649_zpsffe60b82.jpg


photobucket-55115-1353593872718_zpsac929bfb.jpg


photobucket-39557-1353594331542_zps563de6ea.jpg

Nice Pics
What's the HP of the motor?
 
Arc Fault Energy

Arc Fault Energy

This event didn't have a lot of arc flash energy from a clothing perspective.

20kA for 6 cycles is about 8 cal/cm2 IF the arc is 12 inches long (which is unlikely looking at the equipment). This is at 12 inches from the arc.

This was likely in the 4-5 cal range but the door had a bit of pressure due to the current.

I'm basing this on my experience in doing arc flashes in testing. I have about 100,000 under my belt. The calculations would have added multipliers for arc in a box but they are often a little overkill in 15kV equipment like this.

Unlikely to have ignited clothing in my experience. Let me know if I can assist further.
 