2 outlets on single 220v circuit

Status
Not open for further replies.

rookie4now

Senior Member
I have a client that is removing a washer and gas dryer. They are installing a Bosch Axxis washer which indicates 12a 220V 3-prong, and a dryer that indicates 220v 12a 4-prong. It would be fairly easy to add a second outlet onto the existing 30a circuit and have one outlet for the dryer and one for the washer on the same circuit. The only problem I see is that the individual appliances may want 15a protection. Any thoughts?

thank you.
 

dana1028

Senior Member
I have a client that is removing a washer and gas dryer. They are installing a Bosch Axxis washer which indicates 12a 220V 3-prong, and a dryer that indicates 220v 12a 4-prong. It would be fairly easy to add a second outlet onto the existing 30a circuit and have one outlet for the dryer and one for the washer on the same circuit. The only problem I see is that the individual appliances may want 15a protection. Any thoughts?

thank you.

As you said, the individual appliances may [most likely] would require 15- to 20A maximum OCP.

The two receptacles to be installed for this application would both have to be rated 30A per 210.21 [Table 210.21(B)(3)] - now you'd prob. have to change out the cord caps to match up the receptacle(s) - but back to the OCP....mfr. would prob. require max OCP of 15/20.
 

iceworm

Curmudgeon still using printed IEEE Color Books
Location
North of the 65 parallel
Occupation
EE (Field - as little design as possible)
I have a client that is removing a washer and gas dryer. They are installing a Bosch Axxis washer which indicates 12a 220V 3-prong, and a dryer that indicates 220v 12a 4-prong. It would be fairly easy to add a second outlet onto the existing 30a circuit and have one outlet for the dryer and one for the washer on the same circuit. ....
I can't help with your question any more that dana has, but I do have a curiousity question:

With the two appliances showing "220V", are they also 50 Hz?

Pretty rare to see a nameplate with "220V" on anyting made for the US market in the last 50 years.

ice
 

rookie4now

Senior Member
I can't help with your question any more that dana has, but I do have a curiousity question:

With the two appliances showing "220V", are they also 50 Hz?

Pretty rare to see a nameplate with "220V" on anyting made for the US market in the last 50 years.

ice
I'm using 220 generically. The actual range is 208-240.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
You could use the existing circuit as a feeder to a new panel and add the outlets with appropriate over-current protection.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
You could use the existing circuit as a feeder to a new panel and add the outlets with appropriate over-current protection.

That would be a good suggestion but if the washer dryer is in a finished room it may not be a suitable one aesthetically. If it is easy to add a circuit then why not do it right.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
You could use the existing circuit as a feeder to a new panel and add the outlets with appropriate over-current protection.

This may be an easier option depending on what exists to run a new cable. Also the existing 30 amp circuit would need to be 4 wire.
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
The two receptacles to be installed for this application would both have to be rated 30A per 210.21 [Table 210.21(B)(3)]
Remember reading about 220v receptacles in England with build it breakers, but no longer comes up in google.
 

JDB3

Senior Member
If there is an existing washer & gas dryer, and as stated a 30 amp receptacle then why not just change existing receptacles to 220 3 wire & 220 4 wire (again if the existing 30 amp is a 4 wire feed) ...
 

renosteinke

Senior Member
Location
NE Arkansas
Just make the circuit a feeder.

Local overcurrent protection can be easily provided using a Square D QO200TR disconnect ($12) and replacing the included switch with a QO215 breaker ($8) at each appliance.
 

curt swartz

Electrical Contractor - San Jose, CA
Location
San Jose, CA
Occupation
Electrical Contractor
Are you sure you need 2 circuits for this equipment? All of the Bosch units I have run across have a 14-30 (30 amp 120/240 volt) cord and plug on the dryer. On the back of the dryer there is a receptacle to plug the washing machine into. These units are desigend to be installed in existing laundry areas with out modifications to the exsiting electrical.

I just looked at all 6 units at the Bosch web site. They all state that the washing machine plugs into the dryer. The dryer requires a 30 amp 4-wire receptacle.
 
Last edited:

Mike Furlan

Member
Location
Lemont Il
Just make the circuit a feeder.

Local overcurrent protection can be easily provided using a Square D QO200TR disconnect ($12) and replacing the included switch with a QO215 breaker ($8) at each appliance.

If you alter the disconnect, then I think it wouldn't be a listed device anymore.

That is what I was told the last time I tried to do exactly this.

I'll bet Square D sells a device with overcurrent protection, and would rather sell you that.
 

RustyShackleford

Senior Member
Location
NC
Occupation
electrical engineer
Why not just add a fused disconnect (the kind that uses cartridge fuses) for each device ? This wouldn't require altering any device. So the existing 30-amp circuit is run to both disconnects, and then use 15 amp fuses in each disconnect. It seems silly to me to run a new circuit when there's already enough copper going from the main panel to the laundry area. The only issue I see with this is if the washer or dryer specifies a "breaker size" as opposed to "breaker or fuse size" or "fuse size" then (as I understand it) you've got to have a breaker rather than a fuse.
 