It's a loaded questions, but do you think that EPOs are a code requirement for data centers?

Thank you in advance for your help.
 

ron

Senior Member
EPO's are only a code requirement if you want to take advantage of the very minor wiring and equipment leniencies permitted in Article 645. The prerequisites of 645, such as an EPO and much worse, make it something to avoid in my opinion.
 