we recently had an company inspector tell us that a dry type transformer was required to be connected to the conduit system with flex, we cannot find this in the code book? these were on an industrial control rack we piped in with ridgid. Thanks
 

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
we recently had an company inspector tell us that a dry type transformer was required to be connected to the conduit system with flex, we cannot find this in the code book? these were on an industrial control rack we piped in with ridgid. Thanks

It's not in the NEC but it may be in their specifications and or code.
Ask him to show it to you.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Using flex to make the final connection to a transformer is a good wiring practice but not a code requirement. You may find it in some specifications.

Chris
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
What if the transformer is suspended? Flex required or not? If sitting on the floor or on a pad not required as others have stated.

Rob%27s%20Work%20024.JPG
 

jusme123

Senior Member
Location
NY
Occupation
JW
...never liked the idea of 'stacking' transformers. They were designed to dissipate heat, with ambient temp in mind, but the added heat from another transformer stacked below it is what I never liked, it just adds to the higher transformers operating temp..
 

iwire

Moderator
Staff member
Location
Massachusetts
...never liked the idea of 'stacking' transformers. They were designed to dissipate heat, with ambient temp in mind, but the added heat from another transformer stacked below it is what I never liked, it just adds to the higher transformers operating temp..

When you are the one paying for the floor space you will be free to spread them out.
 