We've begun to replace the EMT with RMC. To achieve the 2 hour fire rating the engineers have to chosen to surround the RMC with a 2 hour fire rated enclosure.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
We've begun to replace the EMT with RMC. To achieve the 2 hour fire rating the engineers have to chosen to surround the RMC with a 2 hour fire rated enclosure.

Are you using THHN? The UL document is not real clear to me that it applies to RHH conductors, as it seems to refer to cable assemblies.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
When the conduit run is complete I believe that the redesigned feeders will utilize SimPull THHN.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
That looks like one of the types that is no longer permitted since it lost it's listing.

Agreed. And I know am clear on the fact that it also applies to RHH installed in EMT or RGS, as that is known as FHIT, which is field constructed "Electrical Circuit Protective Systems".
 