Hockeyologist?
Before-Correction, Ph-Ph Voltage and Line-Ampere Unbalance Factors
Calculated VUFs (Voltage-Unbalance-Factor) were 1.26% per NEMA and 1.27% per IEC Standards. The corresponding AUFs (Amperage-Unbalance-Factor) were 6.3% and 6.9% per NEMA and IEC Standards, respectively. The VUF indicates an incorrect tap-setting was probably the problem! Are they 1% steps!
After-Correction, Ph-Ph Voltage and Line Ampere Unbalance Factors
NEMA and IEC VUFs were 0.21% and 0.24% respectively. But the AUFs, were significantly higher, i.e, 11.3% and 11.2% respectively. Thus, if you are sure of your readings there is still a problem, but it is unrelated to supply voltage!
Before & After Correction Ph-Gnd Voltages
VUFs were 0.9% and 1.8% indicating phase-to-ground capacitances are balanced!
Regards, Phil Corso
If it is unrelated to supply voltage, why does the imbalance go away when running on generator?