augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I don't find your Code reference in any of the Code books I have handy.
That said, a plug connection in normally required on cord connected electrical discharge fixtures, but there are exceptions.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Yes, either a cord and plug connection or the luminaire has a luminaire assembly with a strain relief and canopy having a maximum 6" long sectio of raceway for attachment to an outletbox above a suspended ceiling.

Chris
 