Can you mix or add solar panels of different azimuth or orientation in one string?
And if you can supply values for these components
http://www.google.com/search?q="solar+cell+equivalent+circuit"&hl=en&safe=off&client=safari&tbo=u&rls=en&tbm=isch&source=univ&sa=X&ei=dD_GUMDhK6W10QHthYGYBw&ved=0CC4QsAQ&biw=1039&bih=749
for 1 kw and less per sq. meter of panel, you can figure out how bad/good the series circuit will be.
I wouldn't do it. The current from a module is proportional to the sunlight striking it, and the current in the string is limited by the lowest current producing module. In the afternoon when the SW facing modules would be at their peak production the SE facing module would restrict all their output to what it is producing.So what if there's no shading issues, can you still add a panel of different orientation on a series string? ei; one south-east panel orientation added to the 7 panel south west oriented string? The design calls for 3 strings of 8 panels connected to a single inverter.
I wouldn't do it. The current from a module is proportional to the sunlight striking it, and the current in the string is limited by the lowest current producing module. In the afternoon when the SW facing modules would be at their peak production the SE facing module would restrict all their output to what it is producing.
So what if there's no shading issues, can you still add a panel of different orientation on a series string?
Yes, you can. It won't result in the optimum output for the entire array unless you use an inverter that has two separate MPPT channels (they exist), but the negative effect won't be as pronounced as it would if a string were split between modules with different orientations.That was my initial understanding. Em i right that you can still add a string of different orientation in parallel to other strings?
Different orientations may operate at different voltages when separate MPPT channels load them differently based on their available current output. Open circuit voltage is virtually the same as long as there is sunlight irrespective of orientation. I don't know of anything Fronius does that enables differently oriented strings in parallel to be optimally loaded for maximum output if it's not done with multiple MPPT channels, or even how it could be done if the source circuits are paralleled before encountering any active circuitry.I am familiar with the Power-One dual MPPT inverters, but I was not aware of any design feature of the Fronius inverters that would allow them to optimize two different strings operating at different voltages. How do they do that?
I am familiar with the Power-One dual MPPT inverters, but I was not aware of any design feature of the Fronius inverters that would allow them to optimize two different strings operating at different voltages. How do they do that?
I have yet to find more than a couple installers that are familiar with Fronius' "quasi-multiple MPPT" feature!I am familiar with the Power-One dual MPPT inverters, but I was not aware of any design feature of the Fronius inverters that would allow them to optimize two different strings operating at different voltages. How do they do that?