new job starting soon,
Its a 3 storie hotel, with a 100 rooms
wood frame tgi and truss
each room needs 5- 20 amp ckts,
2 for lights 1 for p-tack 1 for gfci and 2 for outlets
33 rooms per floor
No cooking
each room must have a "master lighting disconnect switch"
Looking for the best answer for mc cable.
I would like to cut down the number of homeruns from 160
to avoid a huge bundle/ derateing above main hallway ceilings
back to panel room
If i run 2- 12/3's and 1-12/2 per room
with 2-2p 20 amp breakers and 1 1p breaker
adding time pigtailing the grounded conductor
0r run 2-12/4's and 1-12/2 per room with no time adding the tails
and have choice of breakers 1p or 2p seeing that i an not shareing a grounded conductor
landing each conductor of the same cable on the same phase hence not a true multiwire branch ckt
or am i bound to use a breaker tie for all for poles with the use of 12/4 mc cable?
And yes i would have liked to pipe back to Mech room meaning more fun derateing and time
At the job meeting today ( unable to make)
AHj inspector called for today Arc faults that will be tomorrows battle of 210.12
what would you do?
Its a 3 storie hotel, with a 100 rooms
wood frame tgi and truss
each room needs 5- 20 amp ckts,
2 for lights 1 for p-tack 1 for gfci and 2 for outlets
33 rooms per floor
No cooking
each room must have a "master lighting disconnect switch"
Looking for the best answer for mc cable.
I would like to cut down the number of homeruns from 160
to avoid a huge bundle/ derateing above main hallway ceilings
back to panel room
If i run 2- 12/3's and 1-12/2 per room
with 2-2p 20 amp breakers and 1 1p breaker
adding time pigtailing the grounded conductor
0r run 2-12/4's and 1-12/2 per room with no time adding the tails
and have choice of breakers 1p or 2p seeing that i an not shareing a grounded conductor
landing each conductor of the same cable on the same phase hence not a true multiwire branch ckt
or am i bound to use a breaker tie for all for poles with the use of 12/4 mc cable?
And yes i would have liked to pipe back to Mech room meaning more fun derateing and time
At the job meeting today ( unable to make)
AHj inspector called for today Arc faults that will be tomorrows battle of 210.12
what would you do?