I see those types of installations as a violation of 230.70(A)(1).
Sometimes it's not an NEC issue but a POCO issue. I understand that this might have been a normal installation at the time the house was built. However, the builder who installed this dormer (or add-a-level) created an unsafe situation IMHO. I was not able to copy and paste this sketch from PSE&G but it is on page 104 of this document : http://www.pseg.com/business/builders/new_service/before/pdf/RequirementsElecSvc2005.pdf . It shows their version of how a mast is supposed to be installed with proper clearances.
Hope this helps.
Yes. The disconnect is not "nearest the point of entrance" of the service conductors. The point of entrance is where the conductors penetrate the exterior surface of the building.Service disconnect?:?:?
Yes. The disconnect is not "nearest the point of entrance" of the service conductors. The point of entrance is where the conductors penetrate the exterior surface of the building.
Perhaps the disconnect is below the picture at the required height.
There is no required height for a disconnect, only that the center of the handle be no higher than 6'7".
I think you know that is what I meant. It wasn't meant to be taken so seriously. I posted my response to don_resqcapt19 because the conductors came out from under the siding again and I hadn't thought about a disconnect on such a crappy job. Once he answered I see his point. It is added to the other violations mentioned.