Hello everyone,
I am trying to figure out a way to see how much the capacitors I have installed are saving each month. The building I will be using as an example stands alone, so it makes it easy to see the saving. My utility does not charge for a leading PF and we only pay for a Energy Demand Charge (KVA) and KWH
This building is our central heat plant, so the KW is very consistent every month. From the history of the bills from the previous 4 years the KVA needed was 170, so this is were I got the number for the 150KVAR fixed bank.
Back in May before I installed 150kVAR fixed bank on building main. Copied directly off the Utility bill used for billing.
KVA = 280.35
KW = 231.3
PF = .8250
Last months Bill.
KVA = 250.5
KW = 250.5
PF = 1
To know exactly how much money the capacitors are saving seems very simple, but I feel like its to simple???
To find the money saved from the capacitors last month I would need to do the following:
(sqrt(250.5^2+150^2))=KVA 292
Then subtract last months KVA, which was KVA with fixed bank turned on 250.5KVA from new calculated KVA 292
292-250.5=41.5 KVA
Multiply this number by the amount the Utility charges per KVA in the Demand Charge.
41.5 x $9.7 = $402 dollars saved that month from Fixed cap bank.
Just wanting some feed back. This seems to easy. The reason I am doing this is to track the savings of the Fixed cap banks we currently have on campus and to show the admin that they are important and working. Thank you
KVA = 280.35
KW = 231.3
PF = .8250
Last months Bill.
KVA = 250.5
KW = 250.5
PF = 1
292-250.5=41.5 KVA