Where does it say how many cubic inches mud rings are?
Eddy Current
In the Mike Holt book it says to count a mud ring as 3.60 cubic inches but where are they getting that and what size mud ring? There are all kinds of different size mud rings?
jumper
314.16(A) Box Volume Calculations. The volume of a wiring
enclosure (box) shall be the total volume of the assembled
sections and, where used, the space provided by plaster
rings, domed covers, extension rings, and so forth, that are
marked with their volume or are made from boxes the dimensions
of which are listed in Table 314.16(A).
Eddy Current
But this will be for a test i wont have the physical mud ring in front of me, i thought it might show the different sizes in a table in the NEC.