Great feedback guys...Thankyou...so I went back and fired up all equipment. So happens we have a delta hi leg. 120/240 and c phase 208 nominal. Older system no adjustments on breaker. Crouse hinds .
A phase - 115 amps
B phase - 97 amps
C phase - 20 amps ( hi leg)
Although the balance is way off between phases, would his trip a main? It's a 200 amp and full tilt I'm getting
Say 235 amps but didn't trip this time...
Breaker probably shot ?
They have a small sub off the sub which is fed off a and b phases. Makes sense but when do you stop loading them up.......geeze.
Let me go a little in to how an overload trip operates... First Standard breaker tolerance is + - 10% This is significant of itself, that means a 200 amp breaker may trip as low as 180 amps or never trip as high as 220 amps. That said, an amperage in the call it "near trip setting" could potentially take hours or even days to overcome the intentional delay function of the breaker. Generally breakers have up to three different trip settings. They are referred to as long time (over 1 second), short time .1 to 1 second) and instantaneous (less than 5 cycles). Most commercial and smaller breakers only have long time and instantaneous. There are various methods of intentionally delaying the trip time.. electronic, thermal, hydraulic, pnuematic, geared escapement to name a few. For a 200 amp breaker such as you are using it likely only has long time and instantaneous and the long time is likely a thermal overload. Generally a spring holds the contact open and when a bimetal strip overcomes the opposition of the spring it operates the trip function (honestly, I can explain the actual mechanism of all the other functions more acurrately, but the thermal one is less capable of being "fixed" so we never really needed to "understand it so this may be a little simplistic). The instantaneous trip is generally operated via magnetism or electronic only and works 100% independent of the long time trip. This is part of the importance of all I am explaining. While the trip element for the long time is doing its thing, the instant element sits there, the instant that the amperage exceeds the value to overcome its opposition force, the mechanism operates and bam! So, to solve your problem, the first thing you need to do is determine which function is causing the trip and then go from there.
A couple things:
So an instant trip is going to require an intermittent huge spike in the amperage of about 2000A unless the instant trip element of one breaker is defective.
As mentioned earlier, a long time trip will heat the terminations at least, probably the case of the breaker depending on design.
You likely need a healthy 270 amps or more for a reasonable length of time (over a minute) to even think about tripping the long time. This should be easily detectable with a meter.
Not mentioned earlier, but each pole operates independently of the others, so imbalance doesn't create its own issues, but excess amperage in any one phase does.
I hope this long diatribe helps you to logically approach your troubleshooting, that was my intent.