Panel Problems

Status
Not open for further replies.

347sparky

Member
Location
Iowa
Got a call today about some lights not working in a wood framed storage building, metal siding. There is an outside subpanel (main lug) fed with single phase, 2 hots, a nuetral, no ground, direct burial, 208/120v. Bonding screw is in place, no ground rods. Check voltage and get some weird readings like 200v A leg to nuetral, 0v B leg to nuetral. Turned off all breakers and put on 3 fluke meters A-N, B-N, A-B. Everything looks normal with both legs to nuetral at 120v and A-B at 208v. Turned on a breaker for one 8' HO, viewed the meters and got A-N 30v, B-N 178v, A-B 208v. So I'm thinking I am losing (or lost) the neutral feeding the panel. It is about 300' back to the building where it is tapped from, 100% under asphalt and concrete. Any suggestions as to anything else to check? Is the lack of grounding contributing to this? I'm thinking about trying to megger the N wire, we have a small handheld fluke megger that rarely sees any use.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
130110-2014 EST

Run a test lead from neutral or ground at the main panel to the shed and in your above test measure the voltage from the test lead to the neutral. Almost certainly it will show a large voltage (the voltage drop along the neutral). For a quick check just put a screwdriver in the ground near where you want to test the neutral voltage. If you only had a small offset in the neutral voltage, then the long test lead would be required.

Check for voltage drop at the termination of the neutral at the main panel with the one light load. But do not keep the high voltage on the light very long.

.
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
I
Got a call today about some lights not working in a wood framed storage building, metal siding. There is an outside subpanel (main lug) fed with single phase, 2 hots, a nuetral, no ground, direct burial, 208/120v. Bonding screw is in place, no ground rods. Check voltage and get some weird readings like 200v A leg to nuetral, 0v B leg to nuetral. Turned off all breakers and put on 3 fluke meters A-N, B-N, A-B. Everything looks normal with both legs to nuetral at 120v and A-B at 208v. Turned on a breaker for one 8' HO, viewed the meters and got A-N 30v, B-N 178v, A-B 208v. So I'm thinking I am losing (or lost) the neutral feeding the panel. It is about 300' back to the building where it is tapped from, 100% under asphalt and concrete. Any suggestions as to anything else to check? Is the lack of grounding contributing to this? I'm thinking about trying to megger the N wire, we have a small handheld fluke megger that rarely sees any use.

Keep your hands off the side of that metal building. The kids in the house and the dog in the kennel. The voltage on the side of that building can become quite high. Bad neutral or poor connection someplace. It can usually be found even under asphalt.
 

347sparky

Member
Location
Iowa
Thanks for the replies. I was thinking it had to be the nuetral but might as well get some input from the forum in case I missed something. Looks like I will have to locate a fault finder and tell the customer what the options are.
 