Calculating wall heater loads

Status
Not open for further replies.

crtemp

Senior Member
Location
Wa state
I am going to be wiring a house soon and I can't seem to find a straight answer on how many watts I can run on a 240 volt 20 amp circuit. Do I consider a wall heater circuit to be a continous load? Can I load the circuits up to 4800 watts?

Thanks
 

crtemp

Senior Member
Location
Wa state
Is that the code or just good practice? I thought a continuous load was something that was intended to run for 4 hours or more per day? Is it 4 hours non stop or just 4 hours total?
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
Is that the code or just good practice? I thought a continuous load was something that was intended to run for 4 hours or more per day? Is it 4 hours non stop or just 4 hours total?

Continuous load is a load where the maximum current is expected to continue for 3 hours or more.

A fixed electric space heater is considered a continuous load, by Code. See 424.3(B).
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
Continuous load is a load where the maximum current is expected to continue for 3 hours or more.

A fixed electric space heater is considered a continuous load, by Code. See 424.3(B).

Yes, if you are supplying electric heat, or other continuous loads. If the load is non-continuous you can go up to 4800 watts.

Per the section David cited the wall heaters are a continuous load whether they run for three hours or not.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
True. Whatever the load is if the code requires it to be treated as a continuous load then continuous it is.

But non-continuous loads, and loads not required to be treated as continuous can use the full rating of the circuit. So it is not true that you can only get 3800 watts out of a 20 amp, 240 volt circuit.
 