Sorry, Don ... but there's no way UL made such a balnket statement. Push UL on what you think you heard, and you'll get a lesson in UL's 'engineering double-talk.' Let me use but one example to make the point.
"Classified breakers." Square D says 'use only Square D.' UL says the classified breakers are fine. The little sticker in the panel saying 'use only Square D,' and the disclaimers in the instructions, are not - according to UL- considered as part of the listing and labeling instructions.
Naturally, this does put us in the strange position of having to discern exactly what matters and what is simply marketing.
Likewise, look to any UL standard and you will see it references other standards and codes, things like the NEC. Their standards are specifically written to not compromise anything in those other standards. That's why there was such a fuss over getting 'temporary power taps' listed; it was feared that their use would lead to various NEC violations.
More recently, there has been the entire AFCI furball. Relevant here is the assertion by NEMA that if there is any sort of false trip issue, it is the fault of the appliance- that there has NEVER been a false trip caused by a properly functioning listed appliance. (That's NEMA's assertion, not mine).
We also saw the re-engineering of GFCI's, and a change in the listing standard, about 10 years ago. The GFCI changes were specifically aimed at reducing false trips by motors, refrigerators, etc. There were, at the same time, changes made to the appliance standards. Upshot is: no "current" product should trip a GFCI falsely.
I'll repeat it: UL is not going to list anything whose proper use creates a code violation. Period. What you 'were told' is not UL's position at all.