Hi, I hope that you will understand this. I have never seen anything like this before.
A contractor is installing a generator ( as per Electrical engineered Drawings ) that will pick up some of the load of a 10 story building..
The generator is 175KW with 600 Amp over current protection. They have 3 - 125 amp automatic transfer switches, each goes to a 125 Amp panel. When power is lost the generator comes on. When the generator comes on it does not feed the panels, it feed a 600 Amp emergency panel which has 3 - 125 amp breakers that feeds the 3 panels. The only time that the 600 amp panel is energized is when the generator is on.
What do you think of that design? Do you feel that it meets the 2008 NEC. I feel that it does not meet the requirements of 700.5A . I feel that they need a 600 Amp automatic transfer switch ( which is the full load of the generator ) which would feed the 600 amp Emergency panel.
Any help would be appreciated.
Thanks, Bill
A contractor is installing a generator ( as per Electrical engineered Drawings ) that will pick up some of the load of a 10 story building..
The generator is 175KW with 600 Amp over current protection. They have 3 - 125 amp automatic transfer switches, each goes to a 125 Amp panel. When power is lost the generator comes on. When the generator comes on it does not feed the panels, it feed a 600 Amp emergency panel which has 3 - 125 amp breakers that feeds the 3 panels. The only time that the 600 amp panel is energized is when the generator is on.
What do you think of that design? Do you feel that it meets the 2008 NEC. I feel that it does not meet the requirements of 700.5A . I feel that they need a 600 Amp automatic transfer switch ( which is the full load of the generator ) which would feed the 600 amp Emergency panel.
Any help would be appreciated.
Thanks, Bill