My first post! OK here's the scoop. Two separate PV inverters (SMA5000 and SMA6000) going into a PV-only sub-panel (main lug only and 100A rated). One with a 25A and the other with a 35A breaker. This feeds into a 125A rated main lug only sub-panel (which has multiple other domestic loads) through a 60A backfed breaker in this sub-panel. This sub-panel is protected by an 80A breaker in a 200A main breaker panel located in a separate building.
The system configuration met with resistance from NY incentive folks who review all system documentation prior to installation. Their concern pertains to the 125A main lug only sub-panel with the 60A PV breaker. My contention was that 690.64 B(2) permits me to size as follows: (80+60) </= 125*1.2. Their statement reads as follows:
"In review of your application, required document(s) are missing or need additional information:
[FONT="]Take another look at the 3-line diagram, the 60 amp PV breaker is a violation of NEC 690.64(B)(2) since it in a main lug only sub panel the sum of the main and the PV breakers cannot exceed 120% of the 80amp sub-feed. If the sub panel had an 80 amp main circuit breaker, then it would be 120% of the 125 amp bus rating."
I take this to mean that if you're backfeeding a main lug only sub-panel you cannot use the 120% of bus rating rule but are restricted to 120% of sub-panel breaker rating? Does this make sense to you folks? Your help is greatly appreciated.
[/FONT]
The system configuration met with resistance from NY incentive folks who review all system documentation prior to installation. Their concern pertains to the 125A main lug only sub-panel with the 60A PV breaker. My contention was that 690.64 B(2) permits me to size as follows: (80+60) </= 125*1.2. Their statement reads as follows:
"In review of your application, required document(s) are missing or need additional information:
[FONT="]Take another look at the 3-line diagram, the 60 amp PV breaker is a violation of NEC 690.64(B)(2) since it in a main lug only sub panel the sum of the main and the PV breakers cannot exceed 120% of the 80amp sub-feed. If the sub panel had an 80 amp main circuit breaker, then it would be 120% of the 125 amp bus rating."
I take this to mean that if you're backfeeding a main lug only sub-panel you cannot use the 120% of bus rating rule but are restricted to 120% of sub-panel breaker rating? Does this make sense to you folks? Your help is greatly appreciated.
[/FONT]