I just thought I'd check in and see if anyone has more ideas on possible solutions to a particularly nasty problem.
A friend bought 4 big MCCs for a rock plant and had determined that the AFC was 35kAIC. So when he ordered the MCCs, he ordered them as 42kAIC. Then before he even got them installed, the owner kept adding more and more equipment, he had to keep increasing the service size and transformers, but forgot about the effects that would have on the already ordered MCCs. Now everything is installed and a service company is doing the Arc Flash study and guess what? They now have 58kA AFC. The individual MCC buckets and units are actually OK because they are 65kAIC listed, but the bus bracing is all only 42kA and I've been checking with the factory, it means ripping everything out and changing the bus bracing to increase it (let alone a UL site inspection to put new labels on it). I think changing the transformer(s) in the double ended sub station he put in to ones with higher impedance is out of the realm of possibility. So is changing the MCC structures, we are taling 70+ sections.
My suggestions to him so far:
Any other ideas?
A friend bought 4 big MCCs for a rock plant and had determined that the AFC was 35kAIC. So when he ordered the MCCs, he ordered them as 42kAIC. Then before he even got them installed, the owner kept adding more and more equipment, he had to keep increasing the service size and transformers, but forgot about the effects that would have on the already ordered MCCs. Now everything is installed and a service company is doing the Arc Flash study and guess what? They now have 58kA AFC. The individual MCC buckets and units are actually OK because they are 65kAIC listed, but the bus bracing is all only 42kA and I've been checking with the factory, it means ripping everything out and changing the bus bracing to increase it (let alone a UL site inspection to put new labels on it). I think changing the transformer(s) in the double ended sub station he put in to ones with higher impedance is out of the realm of possibility. So is changing the MCC structures, we are taling 70+ sections.
My suggestions to him so far:
- Hire a PE to do a study and see if he can either replace the Main CBs in the MCCs with Current Limiting versions, or add CL fuses up stream that would bring the AFC at the MCC line terminals down below 42kA. Problem is, 2 of the MCCs have 2000A mains, that ain't no simple thing.
- Start digging trenches and make the cables from the Switchgear to the MCCs artificially longer (might be the least costly solution).
- Add a Reactor ahead of each MCC. I've never done this, just heard about it from others.
Any other ideas?