Hi,
I have a weird situation involving transformers that I could use some advice on.
The load is a 120/240V panel located quite far from the power source. At the moment it is connected to two legs of a 600V three phase generator and stepped down locally with a 15KVA 600V:120/240V transformer. All of that works fine.
The problem is that the client wants change this load over to another source that is 120/208V three phase. This system is also located far from the load so it needs to be stepped up due to voltage drop considerations. I want to use the existing step down transformer but I have a voltage mismatch issue. In an ideal world I would use a 208V:600V single phase transformer and away we go, but I think that is a custom unit. We have a transformer matching the step down at the site but the problem is that that arrangement would expect to be fed with 240V and we are only giving it 208V, so naturally the output voltage is only 208V.
The best option I see so far is to put a 208V to 240V booster transformer ahead of the step up/down system, but I'm wondering if I am missing a simpler option.
thanks for the suggestions.
I have a weird situation involving transformers that I could use some advice on.
The load is a 120/240V panel located quite far from the power source. At the moment it is connected to two legs of a 600V three phase generator and stepped down locally with a 15KVA 600V:120/240V transformer. All of that works fine.
The problem is that the client wants change this load over to another source that is 120/208V three phase. This system is also located far from the load so it needs to be stepped up due to voltage drop considerations. I want to use the existing step down transformer but I have a voltage mismatch issue. In an ideal world I would use a 208V:600V single phase transformer and away we go, but I think that is a custom unit. We have a transformer matching the step down at the site but the problem is that that arrangement would expect to be fed with 240V and we are only giving it 208V, so naturally the output voltage is only 208V.
The best option I see so far is to put a 208V to 240V booster transformer ahead of the step up/down system, but I'm wondering if I am missing a simpler option.
thanks for the suggestions.