can 120 and 277 occupy the same raceway

Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
They can provided all the parameters are in place. See 300.3(C).
Also note 200.(6)(D) & 210.5 (C)
 

DARUSA

Senior Member
Location
New York City
As long both insulations are rated for the maximum voltage applied to the cables, in this case 277volt THHN and the most commons insulation are 600 volt rated .
 