I am the engineer on a pool & gymnasium remodel project. The Owner has experienced one ground fault trip event (on a subpanel) and is stating no further such events are acceptable. Here is some information:
1. There is an existing 480V/3p/4w 1600A service to the building to which we replaced and/or added HVAC equipment and a bank of power factor correction capacitors. Per NEC this has ground fault protection (GFP).
2. There is an existing 208V/3P/4W 600A distribution panel (fed from the service panel via a transformer). This also has GFP (it is the one that tripped). We added one new 100A panel that is fed from this equipment, this new panel feeds only upper level floor boxes and poke throughs for a new fitness area. The distribution panel also feeds an existing administration area where the staff utilize nearly a dozen electric unit heaters, and the existing main server room. The new floor box panel is basically the only new load on this distribution panel.
3. The 600A distribution panel GFP tripped a week ago, after the Owner was cleared to move in but before they actually moved any equipment in. So nothing new had been plugged in. It happened in the middle of the day (about 12:00~12:30) and has not recurred. The electrician dialed the GFP settings up from 100A / 0.1s to ~130A / 0.3s.
4. One other wild card - the reason for the project is the humidity in the building (from the pool) was horrendous. We upgraded the building HVAC, they replaced a few walls because of humidity-induced water damage, there were some overhead pool light fixtures that had rusted stems which were replaced, etc. One of the designers (who has been on this project long since I started here) says he wouldn't be surprised if there were some rusted wires in the system somewhere - sounds like the humidity problem was epic.
I am not seeing any red flags here, except for the ominous "everything we can't see could be rusted straight through" speculation, and of course the Owner's insistence that this not be allowed to happen again or heads will roll. What if anything is reasonable to ask the electrician or Owner to investigate?
A related question - is there any chance that something on the primary side of the transformer could set off the GFP on the secondary side?
Any advice is appreciated. Thanks!
1. There is an existing 480V/3p/4w 1600A service to the building to which we replaced and/or added HVAC equipment and a bank of power factor correction capacitors. Per NEC this has ground fault protection (GFP).
2. There is an existing 208V/3P/4W 600A distribution panel (fed from the service panel via a transformer). This also has GFP (it is the one that tripped). We added one new 100A panel that is fed from this equipment, this new panel feeds only upper level floor boxes and poke throughs for a new fitness area. The distribution panel also feeds an existing administration area where the staff utilize nearly a dozen electric unit heaters, and the existing main server room. The new floor box panel is basically the only new load on this distribution panel.
3. The 600A distribution panel GFP tripped a week ago, after the Owner was cleared to move in but before they actually moved any equipment in. So nothing new had been plugged in. It happened in the middle of the day (about 12:00~12:30) and has not recurred. The electrician dialed the GFP settings up from 100A / 0.1s to ~130A / 0.3s.
4. One other wild card - the reason for the project is the humidity in the building (from the pool) was horrendous. We upgraded the building HVAC, they replaced a few walls because of humidity-induced water damage, there were some overhead pool light fixtures that had rusted stems which were replaced, etc. One of the designers (who has been on this project long since I started here) says he wouldn't be surprised if there were some rusted wires in the system somewhere - sounds like the humidity problem was epic.
I am not seeing any red flags here, except for the ominous "everything we can't see could be rusted straight through" speculation, and of course the Owner's insistence that this not be allowed to happen again or heads will roll. What if anything is reasonable to ask the electrician or Owner to investigate?
A related question - is there any chance that something on the primary side of the transformer could set off the GFP on the secondary side?
Any advice is appreciated. Thanks!