Existing Panelboard Needs Ground

Status
Not open for further replies.

rjken1969

Member
Location
Princeton, NJ
In a recent renovation the contractor on a job found a panelboard that was hidden away out of site. As it turn out the panel is now be moved slightly. I got a large extra as the contractor wants to provide a new feed and include the ground in a new conduit. I know this is the correct way to ground the panel, but will the NEC allow this to be grounded to building steel? Or, perhaps allow the conduit to act as the grounding path? I know the AHJ will have to be involved in the solution, so I want to be prepaired. Any direction as to what section I can reference would be a big help...
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Some metallic conduits are permitted as the EGC for the panel feeder which needs to run with the feeder conductors.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
A connection to building steel cannot be used in place of the code required EGC, as Rob, said, often the metallic raceway is permitted to be used as the code required EGC.
 

LEO2854

Esteemed Member
Location
Ma
In a recent renovation the contractor on a job found a panelboard that was hidden away out of site. As it turn out the panel is now be moved slightly. I got a large extra as the contractor wants to provide a new feed and include the ground in a new conduit. I know this is the correct way to ground the panel, but will the NEC allow this to be grounded to building steel? Or, perhaps allow the conduit to act as the grounding path? I know the AHJ will have to be involved in the solution, so I want to be prepaired. Any direction as to what section I can reference would be a big help...

The pipe can be used but I would run a properly sized EGC anyway.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
....Or, perhaps allow the conduit to act as the grounding path? I know the AHJ will have to be involved in the solution, so I want to be prepaired. Any direction as to what section I can reference would be a big help...
Here's the code section and commentary from the handbook. Not to be argumentative with Harry, just to give another perspective, I would not hesitate to use metal conduit as an EGC.

250.118 Types of Equipment Grounding
Conductors
The equipment grounding conductor run with or enclosing
the circuit conductors shall be one or more or a combination
of the following:
(1) A copper, aluminum, or copper-clad aluminum con-
ductor. This conductor shall be solid or stranded; insu-
lated, covered, or bare; and in the form of a wire or a
busbar of any shape.
(2) Rigid metal conduit.
(3) Intermediate metal conduit.
(4) Electrical metallic tubing.
As specified in 250.118(2), rigid metal conduit (RMC) is an
equipment grounding conductor (EGC), and like other metal
raceways such as intermediate metal conduit (IMC) and
electrical metallic tubing (EMT), it can be used as the sole
EGC without a wire-type equipment grounding conductor
having to be installed in the raceway. As a general rule, the
Code only requires one EGC and it can be any of the types
specified in 250.118(1) through (14). There are specific re-
quirements in the Code, such as 517.13(B), where a wire-
type equipment grounding conductor is required regardless
of the wiring method. However, if a wire-type EGC is in-
stalled in a metal raceway and it is not isolated per
250.96(B), the raceway is in parallel with the wire, and the
combination of the metal raceway and the wire is the EGC
for enclosed circuit(s). Exhibit 250.50 illustrates an installa-
tion where RMC is used as the wiring method for feeder
conductors on the load side of the service equipment. The
wireway can also be used as an equipment grounding con-
ductor without a wire-type EGC per 250.118(13).
 

rjken1969

Member
Location
Princeton, NJ
Thanks Dave, this is exactly what I was looking for. Using the pipe would not be my preference, but in a pinch it will do.


Here's the code section and commentary from the handbook. Not to be argumentative with Harry, just to give another perspective, I would not hesitate to use metal conduit as an EGC.

250.118 Types of Equipment Grounding
Conductors
The equipment grounding conductor run with or enclosing
the circuit conductors shall be one or more or a combination
of the following:
(1) A copper, aluminum, or copper-clad aluminum con-
ductor. This conductor shall be solid or stranded; insu-
lated, covered, or bare; and in the form of a wire or a
busbar of any shape.
(2) Rigid metal conduit.
(3) Intermediate metal conduit.
(4) Electrical metallic tubing.
 