Lighting panel

Status
Not open for further replies.

guschash

Senior Member
Location
Ohio
I have a LP located in a washer and dryer closet. Panel is right over washer. Clothes are hung above washer and dryer on a clothes bar right in front of panel. Bi fold doors hind everything. What are some of the code violations am I looking at. Would 408.16 ....in damp or wet location be one? How about 408.17 easily ignitable material? How about 110.26 working space? I have suggested moving panel out of this closet about three feet and using old panel as a tie box. I would put a meter/disconnect on outside of house and run my 4 wires to new panel, which would now be a sub panel. How's this sound?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Almost assuredly a 100.26 violation. Your plan is a common remedy.
 