Ok so little back round story... at a costumer's house they have a 7kW portable generator that dose not have the grounded (neutral) conductor bonded to the frame. So i put a 2 pole 30 amp breaker in under the 100 amp main breaker, and put the Murray breaker interlock kit in place. Ran 10/3 romex from the panel about 40-50 feet to the back of the house through the outside wall and into the back of a generator inlet power box. I then made up a 20 foot SJO cord (costumer wanted it 20 feet from the house). Now i call the Inspector for that town and he asks me to give him a description of what i did and i told him the above. He then told me he would save me the re-inspection fee and told me to read the Massachusetts amendments (page 11 code article 702.11 (C) ) and said that because I'm not breaking the neutral that i have to have the generator inlet box no more then 10 feet from the panel (which would put the box right in the front of the house) and that the SJO cord can't be any longer then 15 feet. So I reread the article that he was talking about and i believe he is reading it wrong. So i was hoping I could get some input from someone a little more code savvy. Here is what the Massachusetts amendment says...
702.11 (C) Classification of Supply. A generator with a grounded circuit conductor connection as part of its output shall be wired as a separately derived source unless its grounded circuit conductor is not bonded to the frame, or where used to supply a premises wiring system it shall be permitted to be wired as a nonseparately derived source if all of the following conditions are met:
(1) The generator rating does not exceed 15kW.
(2) The generator is connected through a flexible cord and a cord connector to a flanged inlet.
(3) The flexible cord does not exceed 4.5 m (15 ft) in length.
(4) The flanged inlet connection point is not more then 3.0 m (10 ft) from the main bonding jumper or system bonding jumper for the supplied premises.
(5) The point of connection is marked "Disconnect cord when generator is not in service".
(6) Ground-fault protection of equipment has not been installed on any portion of the premises wiring system supplied by the generator.
So the way i read it because the generator's neutral is not bonded to the frame it falls under the "unless" category and doesn't need the neutral broken (transfer switch). But if it was bonded then it would fall under the "or where used" category and then I would have to do (1)-(6).
Any help on this matter would be greatly appreciated.
702.11 (C) Classification of Supply. A generator with a grounded circuit conductor connection as part of its output shall be wired as a separately derived source unless its grounded circuit conductor is not bonded to the frame, or where used to supply a premises wiring system it shall be permitted to be wired as a nonseparately derived source if all of the following conditions are met:
(1) The generator rating does not exceed 15kW.
(2) The generator is connected through a flexible cord and a cord connector to a flanged inlet.
(3) The flexible cord does not exceed 4.5 m (15 ft) in length.
(4) The flanged inlet connection point is not more then 3.0 m (10 ft) from the main bonding jumper or system bonding jumper for the supplied premises.
(5) The point of connection is marked "Disconnect cord when generator is not in service".
(6) Ground-fault protection of equipment has not been installed on any portion of the premises wiring system supplied by the generator.
So the way i read it because the generator's neutral is not bonded to the frame it falls under the "unless" category and doesn't need the neutral broken (transfer switch). But if it was bonded then it would fall under the "or where used" category and then I would have to do (1)-(6).
Any help on this matter would be greatly appreciated.