Hi Guys,

I can't seem to find anywhere in the 2008 NEC where the code states how to identify a wire type system bonding jumper. A screw type is supposed to be green. ...but a wire type? Is it supposed to be green? Black with green tape, for example? Maybe I'm just missing the obvious.


Thanks!
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
A grounding electrode conductor or bonding jumper has no color directive nor does it apply to a screw, clamp, etc. I often mark the ends but it is not necessary
 

Steelhead

Senior Member
Location
Southeastern Wisconsin
Occupation
Industrial Maint/Journeyman
A grounding electrode conductor or bonding jumper has no color directive nor does it apply to a screw, clamp, etc. I often mark the ends but it is not necessary

If you look at 250.28(B) it states that if the system bonding jumper is a screw only it must be green in color. I like to mark the wire with green tape as well.
 