Article 700 and dimming

Status
Not open for further replies.

gdoukas

Member
Location
Orlando, FL
In a theatrical evironment where a dimmer rack is fed with normal/emergency power, can there be normal and emergency loads in the same rack if the rack is UL 924 and can shed the normal loads or does the rack that is designated emergency, only contain those loads which are designated as emergency. Can you point me to the specific code where this stated.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Could you explain a little further how the system is set up and will function?

Welcome to the Forum. :)
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Could you explain a little further how the system is set up and will function?

Welcome to the Forum. :)

I suspect that the dimmer rack controls not only the stage lighting but also the non-exit house lighting so that it can be dimmed smoothly at the start of an act.
The "emergency" (not always used in the correct NEC sense) power is fed to this rack so that full house lighting can restored using backup power. An alternative would be to put the house lighting on an external set of transfer switches so that it goes from controlled brightness on main power to full-on when on backup power.
 

gdoukas

Member
Location
Orlando, FL
Emergency and normal in the same enclosure

Emergency and normal in the same enclosure

The setup is that there is a dimming rack that has normally controlled lighting and emergency lighting in the same rack that are used as normally controlled lights during a theatrical production. The emergency lights when under normal power, such as houselights, are controlled by the operator the same as the normal (theatrical) lights are. When normal power is lost,the rack is then supplied with emergency power through a 1008 transfer. Since the rack is UL924, at that point the rack would shed the normal lights and bring up the emergency loads (house lights). Reading 700.23 this seems acceptable. The issue seems to be the education of the EE and the AHJ. Some manufacturers of dimming equipment supply a seperate "emergency only" rack and a "normal rack" in order to satisfy the parties. I see 700.23 allowing both emergency and normal lighting in the same enclosure. How do you interpret the code (Im in Florida).
 