When modeling large Chiller motors for a fault study should these chiller motors be modeled as motor loads capable of fault current contribution during a fault, or should these be modeled as loads which are not capable of fault current contribution?
I was told once that compressor motors do not contribute any fault current due to the fact that there is no rotating mass. I'm not sure if Chiller motors fall under the same category.
If these motors motor are capable of fault contribution what is the best way to determine equivelent motor HP size. Most chillers I have seen have a kW rating, and/or a RLA, and LRA rating. Is there a rule of thumb for converting this nameplate information to an equivelent Hp size for modeling puposes?
If modeled as a motor what X" is typically used? Is the 17% figure used for single large motors used or would something different be used?
I was told once that compressor motors do not contribute any fault current due to the fact that there is no rotating mass. I'm not sure if Chiller motors fall under the same category.
If these motors motor are capable of fault contribution what is the best way to determine equivelent motor HP size. Most chillers I have seen have a kW rating, and/or a RLA, and LRA rating. Is there a rule of thumb for converting this nameplate information to an equivelent Hp size for modeling puposes?
If modeled as a motor what X" is typically used? Is the 17% figure used for single large motors used or would something different be used?