Service feeder sizing

Status
Not open for further replies.

Shockedby277v

Senior Member
Location
Michigan
208/120v 3 phase system. 400 amp service 500 Cu. Where does it say its ok to run a 500 Cu rated at 380 amps for a 400 amp service?? Thanks
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
It doesn't. What it does say is that if the load is under 380 amps, you can use 500 MCM copper conductors, and protect them with a 400 amp breaker. This does not appear to fit your description, and wouldn't, unless you have a calculation that concludes that the load really is 380 or lower. You have to go two places to get this information: 240.4, and 240.4(B).

That said, if you are talking about a dwelling unit for which the conductors in question supply the entire load, then table 310.15(B)(6) will let you use 400 MCM conductors.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
It doesn't. What it does say is that if the load is under 380 amps, you can use 500 MCM copper conductors, and protect them with a 400 amp breaker. This does not appear to fit your description, and wouldn't, unless you have a calculation that concludes that the load really is 380 or lower. You have to go two places to get this information: 240.4, and 240.4(B).

That said, if you are talking about a dwelling unit for which the conductors in question supply the entire load, then table 310.15(B)(6) will let you use 400 MCM conductors.

Fine point note: True, generally speaking, but not with the OP's 208/120 3 phase service, residential or not.
(I know your post didn't infer that, but I added the note to prevent misunderstanding)
 