PM ON CIRCUIT BREAKERS

Status
Not open for further replies.

bure961

Senior Member
Location
Farmingham, MA
My company just had a westighouse ds or dsl taken out of service last week for pm or testing and brough back the next day.
Should their company furnish the results of the testing and state what was included in the testing ? We were thinking all pm would be at our facility. We are not really sure what type of work should have been done.
If anyone had this type of work to their breakers can you expand on what you know about this work.
 

brian john

Senior Member
Location
Leesburg, VA
For a single circuit breaker we would remove it from site for testing, it is easier to move the circuit breaker to the test set than the test set to the circuit breaker..

Prior to asking for testing and PM, you should asked for a Scope of services included in any work to be performed. We furnish this so there will be no issues later.

PM on a DS, they might remove the cover and see if there are any glaring problems and clean the, vacuum. Assuming this is a draw out CB, they should clean the bus stabs and lubricate per Eaton literature utilizing grease that is specified. All functions of the CB are checked Aux contacts, UV relay or shunt trip.

THe circuit breaker is high current tested, the power contacts are ductored (contact resistance measured) and the circuit breaker is meggered. A detailed test report is submitted to the customer detailing all test and any issues noted.
 

ATSman

ATSman
Location
San Francisco Bay Area
Occupation
Electrical Engineer/ Electrical Testing & Controls
Low Voltage Air Frame Circuit Breaker Test Report

Low Voltage Air Frame Circuit Breaker Test Report

My company just had a westighouse ds or dsl taken out of service last week for pm or testing and brough back the next day.
Should their company furnish the results of the testing and state what was included in the testing ? We were thinking all pm would be at our facility. We are not really sure what type of work should have been done.
If anyone had this type of work to their breakers can you expand on what you know about this work.

See attached typical CB test report for West DS breakers which would be filled out by the testing co after the work Brian stated is completed.

Tony
 

Attachments

  • Circuit Breaker Test Report - Generic.doc
    45.5 KB · Views: 1