Senior Member
- Location
- KY
This industrial building is several years old and has an original 2500A service (underground). In the last 5 years an additional service was added to the building. The service is overhead and is 2500A as well. The services are both fed onto the property as a single customer owned 12.47kV system. Customer is metered at 12.47kV on the pole before the two services are paralleled in the building, therefore there is only one meter to satisfy. We are installing a 2000KVAr bank that is fed primary 12.47kV. Our original intention was to place the bank on the immediate pole after the meter so it will catch the lines before they split into two parallel lines (old and new). We have decided there is too much on the pole and it would be too cluttering to do so. There is plenty of room to place the bank on one of the paralleled lines going into the building. Since the bank is only on 1 header entering the building, the customer is concerned there may be issues with installing the full KVAr on half of the capacity. I assured the customer that the VAR will flow where they are needed to satisfy the meter. Also, I assured him that there will be no over voltage issues. Furthermore, each paralleled section is fused appropriately. Am I over looking any possible issues that can arise due to the bank not being immediately after the meter? Any thoughts.