Grounding requirements for an unattached garage.

Status
Not open for further replies.

mudcat555

Member
Location
Mentor, Ohio (25 miles east of Cleveland)
Occupation
Retired Electrician IBEW Local 38
Residential unattached garage. Feeding a garage sub-panel from main panel in house basement. Under-ground pvc out to garage. Do I need to pull a ground wire along with the feeders, or do I pound a ground rod for the garage panel and get my ground from that ... or both? The code "exceptions" have me confused.
 

iwire

Moderator
Staff member
Location
Massachusetts
Under the current NEC you must pull an EGC with the feeder and you must establish a grounding electrode system out at the garage. The GES will tie into the EGC at the garage.

You do not bond the neutral to EGC at the garage.
 
Residential unattached garage. Feeding a garage sub-panel from main panel in house basement. Under-ground pvc out to garage. Do I need to pull a ground wire along with the feeders, or do I pound a ground rod for the garage panel and get my ground from that ... or both? The code "exceptions" have me confused.

Both, unattached is the key word. the sub panel will be treated as such.
 