... I was under the understanding that the equipment grounding conductor had to be 1/0 or greater.
... I bow to experience
Well experience teaches us that experience and the Code do not always agree. So your
statement amounts to meaningless :happyyes:
While iwire Bob quoted a section in defense of EGC's not required to be 1/0AWG and larger to be run in parallel, let me counter that with...
310.10(H) said:
(5) Equipment Grounding Conductors. Where parallel
equipment grounding conductors are used, they shall be sized
in accordance with 250.122. Sectioned equipment grounding
conductors smaller than 1/0 AWG shall be permitted in multiconductor
cables in accordance with 310.104, provided the
combined circular mil area of the sectioned equipment
grounding conductors in each cable complies with 250.122.
This implies that unless specified as hereinabove, EGC's must be 1/0AWG and larger to be permitted in parallel.
PS: Compliance with 250.122 has no bearing on the matter, as it simply requires EGC's
no smaller than listed in Table 250.122, and does not prohibit upsizing the smaller EGC sizes to 1/0AWG for compliance with other sections.