Receptacle Tension Testing

Status
Not open for further replies.

wmeek

Senior Member
Location
Texas
Occupation
Electrician
Was wanting to know if someone might be able to help with receptacle tension testing. Where can you find the tension setting on regular an hospital grade receptacles. Have a surgery center facility that gets yearly inspections an are requiring a tension test on all receptacles.
 

Smart $

Esteemed Member
Location
Ohio
Was wanting to know if someone might be able to help with receptacle tension testing. Where can you find the tension setting on regular an hospital grade receptacles. Have a surgery center facility that gets yearly inspections an are requiring a tension test on all receptacles.
Copied from Leviton RTT99 Instruction Sheet...

NFPA 99 - Health Care Facilities: Paragraph 3-3.3.3
Receptacle Testing in Patient Care Areas, subparagraph
(d) specifies ?The retention force of the
grounding blade of each electrical receptacle (except
locking-type receptacles) shall be not less than 115 g
(4.0 oz)".
 