It's now my trashed chart but as I recall it only showed L-L
Post 9 & 10 sure confused my issue.
I was happy with Jim's 5820.. now I,m back to 11,000 ????
Not sure if I need to clarify... it's a 12kv pad with a 480Y/277 secondary.
Julius or Topgone, think one of you guys can talk down to my level ???
I am sorry. Been out lately.
Looking at your numbers, it's easy to see that what you got is a transformer secondary that can be wired Y (480V) or YY(277V). Your secondary fault current will now be twice your calculated bolted fault current at 277V than if you wired it at 480V. Either ways, you have the right formula; just make sure you wired the secondaries the way you based your calcs on, i.e. the bolted fault current will be 5820 X 1.1 (6402A) @ 480V or 10,085 X 1.1 (11,093A) @ 277V.