Limit as to how many taps can be on one circuit other than following the six hand switch rule.
Minimum size for example (paralleled conductors can be no smaller than 1/0.)

Just looking to see if I'm missing SPECIFICS printed in the NEC.
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
There is no limit to the number of taps to a feeder. Of course your total load cannot exceed the rating of the feeder. Nor is there a minimum size allowable conductor for feeder taps.
 