You disagree? Do you disagree that there is a disagreement, because there very certainly IS a disagreement.
I disagreed with Goldigger's statement that there are two different chains of reasoning that are consistent with the code. Exeltech's whitepaper is not consistent with the code, in my opinion.
It is worth noting that the whitepaper does not even appeal to 240.5(B)(2), as some have done in this thread. The extent of the argument in the white paper is this:
"
NEC 690.8 (?Circuit Sizing and Current?) focuses on PV source and output circuit currents, and stand-alone inverter input circuit
currents. Inasmuch as AC Modules have no exposed DC circuits, this section is not applicable to PVAC Modules."
The word 'focuses' serves as a nice little bit of obfuscation, intentional or not, that serves to ignore those parts (mainly 690.8(A)(3)) that apply to inverter output circuits. I don't know where the writer gets the notion that these clauses focus on stand-alone inverters.
It really just seems as if either the writer was not very familiar with the code, or if he was hoping that the reader would not be.
At this point I truly think the best thing to do is contact Intertek and probably Exeltech.
Well if I were actually installing this stuff, or if I were an AHJ inspecting it, I might do that. I think our OP's decision to following 690.8 regardless of the Helios instructions is a wise one.