3 phase 208 service serving 12 appartments, the appartments are using 2 phases only. Does this look right?
1488 sq ft appartmen
lighting, 1488x3va= 4,464va
2 appliance= 3,000va
refridgerator= 1,500va
microwave= 1,500va
garbage disp= 1,000va
dish washer= 1,500va
heat= 6,240va
dryer= 5,000va
range= 10,000va
@ 100% = 34,204va

34204va x 12 units= 410,448va
410440va/208v= 1,973.3a
1973.3a/1.732= 1,139.31a
1,139.31 x 41%(12 units)= 467.12a
467a + 1-100a house panel= 567a
600a main
 

kwired

Electron manager
Location
NE Nebraska
He also threw in 100 amps for the house panel, pretty good chance it is a 100 amp panel with less than 100 amps of load if you do the calculations.

Maybe the laundry is on the house panel but the owner doesn't want to pay electric bill for dryers, so they have to bring clothes back to their unit to dry them. Seems odd but could happen I guess.
 