overhead garage feed

Status
Not open for further replies.

bobbymari

Senior Member
Location
los angeles ca
have to refeed overhead garage. code compliance came by property and gave ok to refeed overhead. in garage there is only one receptacle and a light. my question is this. using a triplex wire and resplicing at both ends, how do you get your ground? shall i use one of the two wires as a neutral and bond the messenger wire to the conduits? its only a 120 feed. i normally do these underground so not exactly familiar with this install, underground not an option in this case
 

John120/240

Senior Member
Location
Olathe, Kansas
If the inspector said "Go ahead and do it" I would use a three wire triplex. One of the insulated wires is hot, one insulated wire is neutral,

the bare wire would be ground. For 120 V receptacle this should be fine.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
120' is a long stretch for that wire. Can you get the clearances needed? Not sure of the stress it will put on the wire at that distance-- what size triplex are you pulling
 