tim89s
Member
- Location
- Brush Prairie WA
I realize you bond xo on the secondary side of a transformer. Let's say you have a delta wye
transformer and all your loads on the secondary are three phase. What would happen if you
didn't bond xo to ground. I have heard that no fault would occur since no reference to ground was made. I am confused, you would still have the ground from the primary side tied to the
ground of the secondary. Wouldn't the primary side ocpd trip? I understand the xo bond gives
you a lower impedance to ground but I would still think the primary side ocpd would trip in the event of a ground fault.
Please help to clarify
Thank you