Voltage Drop Factors:

Status
Not open for further replies.

SJRibsman

Member
Location
south Dakota
Hello, I have recentl aquired an Electrician's Calculations Manual from the library, and I am at the chapter on Voltage Drop. The question I have concerns the 2KIL, divided by the CM. As I recall the K (constant) was 1.93 for cu. and 3,18 for al. The book shows 11 and 18 for al.
 

Gregg Harris

Senior Member
Location
Virginia
Occupation
Electrical,HVAC, Technical Trainer
Hello, I have recentl aquired an Electrician's Calculations Manual from the library, and I am at the chapter on Voltage Drop. The question I have concerns the 2KIL, divided by the CM. As I recall the K (constant) was 1.93 for cu. and 3,18 for al. The book shows 11 and 18 for al.


Recheck your # from chapter 9 in NEC Table # 8

11 and 18 are correct K at 77-121 degrees F
 