An electrical contractor connecting our 2mW generator (480v 3ph 4w ) to our existing transfer switchboard is telling me he can use 5 conductors per phase of 444.4 kMCM RHW-2 to carry the 3000a output of the generator. The run is about 35 l/f from genset to swbd. The cable will be installed in ladder type cable tray. The contractor intends to use mechanical al/cu 75 degree C lugs. He tells me this is all permissible and after looking at sales literature from Mfg of the cable and reading 310.15 table in NEC, I'm not convinced. Questions: 1) is his use of the 90deg C "free air" table correct when using 75 deg C mechanical lugs on stranded RHW-2. (2) is it even permissible to use mechanical lugs on stranded cable like this? Experts, please chime in.