multi wire branch circuit grounding

Status
Not open for further replies.

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
1 2" emt. room for additional circuits.
You do realize that the 12 current carrying conductors you are already installing are only good for 50% of their 90 deg rating and if you add 8 more it will even be less don't you?

Meaning if you are using # 12 THWN conductors they are only good for 15 amps before you add any more.

Roger
 