Looking at a VFD project where the VFD and motors are purchased and installed by others and the drawings show a 5% line and load reactor for VFD's where the motors are being installed up to 350' away, as I continue reading there is also a voltage drop requirement requreing not more than 5% VD at the motor terminals, however at full oputput, my understanding is that the 5% line reactor will introudce 5% VD across it, with that the wire will have to be increased to meet the spcification requriements. with the input voltage hovering around 477V this would mean as soon as I leave the drive I will be around 453V, with the motor being rated at 460V [inverter duty] designed to operate at +/- 10% with the low side being approx. 414V if I can maintain not more than 3% VD from the VFD to the motor it would still be within the operating charasterstics of the motor with some flexibility for utility / system voltage sags that may occur, just wanted to see others experience with voltage drop and output reactors, on VFD's.