So recently I noticed an electrician switching on/off a 480V MCC main breaker for maintenance. The arc flash label on the breaker panel is marked 60 cal. I told him it's best to get a flash suit on for the following two reasons
1. Main breakers like this haven't been exercised for a long time, we don't know its condition
2. Arc flash cal. is high in this case, and the 480V panels are NON arc blast resistant, and I told him if there was a fault, it wouldn't make a difference if you had that panel in front of you or not.
His argument of not wearing the flash suit:
I only need the flash suit if I rack the breaker in/out, since there's no racking in/out action, I don't need the flash suit.
So, what's the correct action in this case? Any particular place on the NFPA 70E we can look to seek some clarifications?
Thanks.
1. Main breakers like this haven't been exercised for a long time, we don't know its condition
2. Arc flash cal. is high in this case, and the 480V panels are NON arc blast resistant, and I told him if there was a fault, it wouldn't make a difference if you had that panel in front of you or not.
His argument of not wearing the flash suit:
I only need the flash suit if I rack the breaker in/out, since there's no racking in/out action, I don't need the flash suit.
So, what's the correct action in this case? Any particular place on the NFPA 70E we can look to seek some clarifications?
Thanks.