Ok I'm new to the forum and there is a lot of info in my question so bare with me. I looked at a tanning salon the other day that had 8 beds and a spray tan booth. The building had a 300A 208 3 phase service. The beds are on two-pole breakers and had a 208-230 buck boost trasformers. 1.5kva for the three big beds and 1kva for the five small beds. Here are the actual amprobe readings.
1-67A 2-34A 3-34A 4-15A 5-28A 6-28A
7-28A 8-66A 9-52A (rounded up)
There is also 22A of lighting load and a 50A three phase A/C. The utility demand meter shows peak demand of 57kw. The owner says there are times were all beds and the A/C are running together. My problem is the owner hired an electrical engineer to tell him if he could remove the three 28A beds and replace them with a 67A bed and two 34A beds. The electrical engineer never left the office and based all calculations off of the max demand. I think that is the wrong way to figure it being the max demand is based on a 15min window. Your thoughts?
1-67A 2-34A 3-34A 4-15A 5-28A 6-28A
7-28A 8-66A 9-52A (rounded up)
There is also 22A of lighting load and a 50A three phase A/C. The utility demand meter shows peak demand of 57kw. The owner says there are times were all beds and the A/C are running together. My problem is the owner hired an electrical engineer to tell him if he could remove the three 28A beds and replace them with a 67A bed and two 34A beds. The electrical engineer never left the office and based all calculations off of the max demand. I think that is the wrong way to figure it being the max demand is based on a 15min window. Your thoughts?