Light bulbs burning out
I got a call from a fit club and they said some fluorescents and halogen bulbs are burning out. Now a pendant with a small halogen just blew up like a fire cracker. I have no idea where to start. Voltage from street?
augie47
Tennessee
Good place to start, but be sure to check at the lamp location also. Deficiencies in the system could cause a higher voltage anywhere in the system.
Multitude of possibilities but I would rule out a voltage issue first.
POCO's voltage might be a bit high, or a loose neutral situation can cause a high voltage.
Make sure to check it more than once with various equipment in operation.
LEO2854
Esteemed Member
Ma
Check the panel where the circuits are coming from , there could be heat damage from over loading.
Welcome to the forum.:thumbsup:
Dennis Alwon
Chapel Hill, NC
Retired Electrical Contractor
Look for a loose neutral as that can increase the voltage on one leg while decreasing it on the other. It may be just slightly loose.
ATSman
ATSman
San Francisco Bay Area
Electrical Engineer/ Electrical Testing & Controls
I agree with Dennis.
Loose or broken neutral at the 20A breaker subpanel.
If that looks ok then check the XO to ground connection at the supply transformer which
can raise the phase to ground voltages to the lights....been there...done that:)
Sierrasparky
USA
Electrician ,contractor
What are the voltages.
It's all speculation at this point