Hello,
I need to size a contactor for the switching of a transformer. The transformer is 208V 3ph 30kVA. The inrush, according to the manufacturer is ~410A. I'm looking at an ABB catalog and I'm seeing ratings for HP, lighting, and resistive loads but not for a transformer and I'm wondering how to handle that.
The catalog says: "Switching of transformers: This application is characterized by high current peaks on contactor closing due to magnetization phenomena. The corresponding utilization category according to IEC 947-4-1 is AC-6a. Ratings are derived from test-values for AC-3 or AC-4 according to formula given in IEC 947-4-1."
I think the catalog is just quoting IEC and not making a statement of their own.
So does that mean to take an AC-3 or AC-4 rating and apply an IEC formula to determine which contactor to use for a transformer?
I need to size a contactor for the switching of a transformer. The transformer is 208V 3ph 30kVA. The inrush, according to the manufacturer is ~410A. I'm looking at an ABB catalog and I'm seeing ratings for HP, lighting, and resistive loads but not for a transformer and I'm wondering how to handle that.
The catalog says: "Switching of transformers: This application is characterized by high current peaks on contactor closing due to magnetization phenomena. The corresponding utilization category according to IEC 947-4-1 is AC-6a. Ratings are derived from test-values for AC-3 or AC-4 according to formula given in IEC 947-4-1."
I think the catalog is just quoting IEC and not making a statement of their own.
So does that mean to take an AC-3 or AC-4 rating and apply an IEC formula to determine which contactor to use for a transformer?